MODBUS® Protocol With Visual C# 2010
  • MODBUS® Protocol With Visual C# 2010
    MODBUS® Protocol Description
    MODBUS® Protocol is a messaging structure, widely used to establish master-slave communication between intelligent devices. A MODBUS message sent from a master to a slave contains the address of the slave, the 'command' (e.g. 'read register' or 'write register'), the data, and a check sum (LRC or CRC).
    Since Modbus protocol is just a messaging structure, it is independent of the underlying physical layer. It is traditionally implemented using RS232, RS422, or RS485
    The Request
    The function code in the request tells the addressed slave device what kind of action to perform. The data bytes contains any additional information that the slave will need to perform the function. For example, function code 03 will request the slave to read holding registers and respond with their contents. The data field must contain the information telling the slave which register to start at and how many registers to read. The error check field provides a method for the slave to validate the integrity of the message contents.
    The Response
    If the slave makes a normal response, the function code in the response is an echo of the function code in the request. The data bytes contain the data collected by the slave, such as register values or status. If an error occurs, the function code is modified to indicate that the response is an error response, and the data bytes contain a code that describes the error. The error check field allows the master to confirm that the message contents are valid.
    Controllers can be setup to communicate on standard Modbus networks using either of two transmission modes: ASCII or RTU.
    ASCII Mode
    When controllers are setup to communicate on a Modbus network using ASCII (American Standard Code for Information Interchange) mode, each eight-bit byte in a message is sent as two ASCII characters. The main advantage of this mode is that it allows time intervals of up to one second to occur between characters without causing an error.
    Coding System
    Hexadecimal ASCII printable characters 0 ... 9, A ... F
    Bits per Byte
    1 start bit
    7 data bits, least significant bit sent first
    1 bit for even / odd parity-no bit for no parity
    1 stop bit if parity is used-2 bits if no parity
    Error Checking
    Longitudinal Redundancy Check (LRC)
    RTU Mode
    When controllers are setup to communicate on a Modbus network using RTU (Remote Terminal Unit) mode, each eight-bit byte in a message contains two four-bit hexadecimal characters. The main advantage of this mode is that its greater character density allows better data throughput than ASCII for the same baud rate. Each message must be transmitted in a continuous stream.
    Coding System
    Eight-bit binary, hexadecimal 0 ... 9, A ... F
    Two hexadecimal characters contained in each eight-bit field of the message
    Bits per Byte
    1 start bit
    8 data bits, least significant bit sent first
    Error Check Field
    Cyclical Redundancy Check (CRC)
    In ASCII mode, messages start with a colon ( : ) character (ASCII 3A hex), and end with a carriage return-line feed (CRLF) pair (ASCII 0D and 0A hex).
    The allowable characters transmitted for all other fields are hexadecimal 0 ... 9, A ... F. Networked devices monitor the network bus continuously for the colon character. When one is received, each device decodes the next field (the address field) to find out if it is the addressed device.
    Intervals of up to one second can elapse between characters within the message. If a greater interval occurs, the receiving device assumes an error has occurred. A typical message frame is shown below.
    Start Address Function Data LRC End
    : 2 Chars 2 Chars N Chars 2 Chars CR LF
    RTU Framing
    In RTU mode, messages start with a silent interval of at least 3.5 character times. This is most easily implemented as a multiple of character times at the baud rate that is being used on the network (shown as T1-T2-T3-T4 in the figure below). The first field then transmitted is the device address.
    The allowable characters transmitted for all fields are hexadecimal 0 ... 9, A ... F. Networked devices monitor the network bus continuously, including during the silent intervals. When the first field (the address field) is received, each device decodes it to find out if it is the addressed device.
    Following the last transmitted character, a similar interval of at least 3.5 character times marks the end of the message. A new message can begin after this interval.
    The entire message frame must be transmitted as a continuous stream. If a silent interval of more than 1.5 character times occurs before completion of the frame, the receiving device flushes the incomplete message and assumes that the next byte will be the address field of a new message.
    Similarly, if a new message begins earlier than 3.5 character times following a previous message, the receiving device will consider it a continuation of the previous message. This will set an error, as the value in the final CRC field will not be valid for the combined messages. A typical message frame is shown below.
    Start Address Function Data CRC End
    3.5 Char time 8 Bit 8 Bit N * 8Bit 16 Bit 3.5 Char time
    Address Field
    The address field of a message frame contains two characters (ASCII) or eight bits (RTU). The individual slave devices are assigned addresses in the range of 1 ... 247.
    Function Field
    The Function Code field tells the addressed slave what function to perform.
    The following functions are supported by Modbus poll
    01 READ COIL STATUS
    02 READ INPUT STATUS
    03 READ HOLDING REGISTERS
    04 READ INPUT REGISTERS
    05 WRITE SINGLE COIL
    06 WRITE SINGLE REGISTER
    15 WRITE MULTIPLE COILS
    16 WRITE MULTIPLE REGISTERS
    The data field contains the requested or send data.
    Contents of the Error Checking Field
    Two kinds of error-checking methods are used for standard Modbus networks. The error checking field contents depend upon the method that is being used.
    ASCII
    When ASCII mode is used for character framing, the error-checking field contains two ASCII characters. The error check characters are the result of a Longitudinal Redundancy Check (LRC) calculation that is performed on the message contents, exclusive of the beginning colon and terminating CRLF characters.
    The LRC characters are appended to the message as the last field preceding the CRLF characters.
    LRC Example Code
    RTU
    When RTU mode is used for character framing, the error-checking field contains a 16-bit value implemented as two eight-bit bytes. The error check value is the result of a Cyclical Redundancy Check calculation performed on the message contents.
    The CRC field is appended to the message as the last field in the message. When this is done, the low-order byte of the field is appended first, followed by the high-order byte. The CRC high-order byte is the last byte to be sent in the message.
    CRC Example Code
    ________________________________________
    Function 01 (01hex) Read Coils
    Reads the ON/OFF status of discrete coils in the slave.
    Request
    The request message specifies the starting coil and quantity of coils to be read.
    Example of a request to read 10...22 (Coil 11 to 23) from slave device address 4:
    Field Name RTU (hex) ASCII Characters
    Header None : (Colon)
    Slave Address 04 0 4
    Function 01 0 1
    Starting Address Hi 00 0 0
    Starting Address Lo 0A 0 A
    Quantity of Coils Hi 00 0 0
    Quantity of Coils Lo 0D 0 D
    Error Check Lo DD LRC (E 4)
    Error Check Hi 98
    Trailer None CR LF
    Total Bytes 8 17
    Response
    The coil status response message is packed as one coil per bit of the data field. Status is indicated as: 1 is the value ON, and 0 is the value OFF. The LSB of the first data byte contains the coil addressed in the request. The other coils follow toward the high-order end of this byte and from low order to high order in subsequent bytes. If the returned coil quantity is not a multiple of eight, the remaining bits in the final data byte will be padded with zeroes (toward the high-order end of the byte). The byte count field specifies the quantity of complete bytes of data.
    Example of a response to the request:
    Function 01 0 1
    Byte Count 02 0 2
    Data (Coils 7...10) 0A 0 A
    Data (Coils 27...20) 11 1 1
    Error Check Lo B3 LRC (D E)
    Error Check Hi 50 None
    Trailer None CR LF
    Total Bytes 7 15
    Function 02(02hex) Read Discrete Inputs
    Reads the ON/OFF status of discrete inputs in the slave.
    Request
    The request message specifies the starting input and quantity of inputs to be read.
    Example of a request to read 10...22 (input 10011 to 10023) from slave device address 4:
    Function 02 0 2
    Quantity of inputs Hi 00 0 0
    Quantity of inputs Lo 0D 0 D
    Error Check Lo 99 LRC (E 3)
    Error Check Hi 98
    Trailer None CR LF
    Total Bytes 8 17
    Response
    The input status response message is packed as one input per bit of the data field. Status is indicated as: 1 is the value ON, and 0 is the value OFF. The LSB of the first data byte contains the input addressed in the request. The other inputs follow toward the high-order end of this byte and from low order to high order in subsequent bytes. If the returned input quantity is not a multiple of eight, the remaining bits in the final data byte will be padded with zeroes (toward the high-order end of the byte). The byte count field specifies the quantity of complete bytes of data.
    Function 02 0 2
    Byte Count 02 0 2
    Data (Inputs 17...10) 0A 0 A
    Data (Inputs 27...20) 11 1 1
    Error Check Lo B3 LRC (D D)
    Error Check Hi 14 None
    Trailer None CR LF
    Total Bytes 7 15
    Function 03 (03hex) Read Holding Registers
    Read the binary contents of holding registers in the slave.
    Request
    The request message specifies the starting register and quantity of registers to be read.
    Example of a request to read 0...1 (register 40001 to 40002) from slave device 1:
    Slave Address 01 0 1
    Function 03 0 3
    Starting Address Lo 00 0 0
    Quantity of Registers Hi 00 0 0
    Quantity of Registers Lo 02 0 2
    Error Check Lo C4 LRC (F A)
    Error Check Hi 0B
    Trailer None CR LF
    Total Bytes 8 17
    Response
    The register data in the response message are packed as two bytes per register, with the binary contents right justified within each byte. For each register the first byte contains the high-order bits, and the second contains the low-order bits.
    Function 03 0 3
    Byte Count 04 0 4
    Data Hi 00 0 0
    Data Lo 06 0 6
    Data Hi 00 0 0
    Data Lo 05 0 5
    Error Check Lo DA LRC (E D)
    Error Check Hi 31 None
    Trailer None CR LF
    Total Bytes 8 19
    Function 04 (04hex) Read Input Registers
    Read the binary contents of input registers in the slave.
    Request
    Example of a request to read 0...1 (register 30001 to 30002) from slave device 1:
    Function 04 0
    Error Check Lo 71 LRC (F 9)
    Error Check Hi CB
    Trailer None CR LF
    Total Bytes 8 17
    Response
    Function 04 0 4
    Byte Count 04 0 4
    Data Hi 00 0 0
    Data Lo 06 0 6
    Data Hi 00 0 0
    Data Lo 05 0 5
    Error Check Lo DB LRC (E C)
    Error Check Hi 86 None
    Trailer None CR LF
    Total Bytes 9 19
    Function 05 (05hex) Write Single Coil
    Writes a single coil to either ON or OFF.
    Request
    The request message specifies the coil reference to be written. Coils are addressed starting at zero-coil 1 is addressed as 0.
    The requested ON / OFF state is specified by a constant in the request data field. A value of FF 00 hex requests the coil to be ON. A value of 00 00 requests it to be OFF. All other values are illegal and will not affect the coil.
    Here is an example of a request to write coil 173 ON in slave device 17:
    Slave Address 11 1 1
    Function 05 0 5
    Coil Address Hi 00 0 0
    Coil Address Lo AC A C
    Write Data Hi FF 0 0
    Write Data Lo 00 F F
    Error Check Lo 4E LRC (3 F)
    Error Check Hi 8B
    Trailer None CR LF
    Total Bytes 8 17
    Response
    The normal response is an echo of the request, returned after the coil state has been written.
    Function 05 0 5
    Error Check Hi 8B
    Trailer None CR LF
    Total Bytes 8 17
    Function 06 (06hex) Write Single Register
    Writes a value into a single holding register.
    Request
    The request message specifies the register reference to be Written. Registers are addressed starting at zero-register 1 is addressed as 0.
    The requested Write value is specified in the request data field. Here is an example of a request to Write register 40002 to 00 03 hex in slave device 17.
    Function 06 0 6
    Register Address Hi 00 0 0
    Register Address Lo 01 0 1
    Write Data Hi 00 0 0
    Write Data Lo 03 0 3
    Error Check Lo 9A LRC (E 5)
    Error Check Hi 9B
    Trailer None CR LF
    Total Bytes 8 17
    Response
    The normal response is an echo of the request, returned after the register contents have been written.
    Function 06 0 6
    Coil Address Lo 01 0 1
    Error Check Hi 9B
    Trailer None CR LF
    Total Bytes 8 17
    Function 15 (0Fhex) Write Multiple Coils
    Writes each coil in a sequence of coils to either ON or OFF.
    Request
    The request message specifies the coil references to be written. Coils are addressed starting at zero-coil 1 is addressed as 0.
    The requested ON / OFF states are specified by contents of the request data field. A logical 1 in a bit position of the field requests the corresponding coils to be ON. A logical 0 requests it to be OFF.
    Below is an example of a request to write a series of ten coils starting at coil 20 (addressed as 19, or 13 hex) in slave device 17.
    The request data contents are two bytes: CD 01 hex (1100 1101 0000 0001 binary). The binary bits correspond to the coils in the following way:
    Bit: 1 1 0 0 1 1 0 1 0 0 0 0 0 0 0 1
    Coil: 27 26 25 24 23 22 21 20 - - - - - - 29 28
    The first byte transmitted (CD hex) addresses coils 27 ... 20, with the least significant bit addressing the lowest coil (20) in this set.
    The next byte transmitted (01 hex) addresses coils 29 and 28, with the least significant bit addressing the lowest coil (28) in this set. Unused bits in the last data byte should be zero-filled.
    Function 0F 0 F
    Coil Address Lo 13 1 3
    Quantity of Coils Lo 0A 0 A
    Byte Count 02 0 2
    Write Data Hi CD C D
    Write Data Lo 01 0 1
    Error Check Lo BF LRC (F 3)
    Error Check Hi 0B
    Trailer None CR LF
    Total Bytes 11 23
    Response
    The normal response returns the slave address, function code, starting address, and number of coils written. Here is an example of a response to the request shown above
    Function 0F 0 F
    Error Check Lo 26 LRC (C 3)
    Error Check Hi 99
    Trailer None CR LF
    Total Bytes 8 17
    Function 16 (10hex) Write Multiple Registers
    Writes values into a sequence of holding registers
    Request
    The request message specifies the register references to be written. Registers are addressed starting at zero-register 1 is addressed as 0.
    The requested write values are specified in the request data field. Data is packed as two bytes per register.
    Here is an example of a request to write two registers starting at 40002 to 00 0A and 01 02 hex, in slave device 17:
    Function 10 1 0
    Starting Address Lo 01 0 1
    Byte Count 04 0 4
    Data Hi 00 0 0
    Data Lo 0A 0 A
    Data Hi 01 0 1
    Data Lo 02 0 2
    Error Check Lo C6 LRC (C B)
    Error Check Hi F0
    Trailer None CR LF
    Total Bytes 13 23
    Response
    The normal response returns the slave address, function code, starting address, and quantity of registers written. Here is an example of a response to the request shown above.
    Function 10 1 0
    Error Check Lo 12 LRC (D C)
    Error Check Hi 98
    Trailer None CR LF
    Total Bytes 8 17
    LRC Example Code
    This function is an example how to calculate a LRC BYTE using the C language.
    BYTE LRC (BYTE *nData, WORD wLength)
    BYTE nLRC = 0 ; // LRC char initialized
    for (int i = 0; i < wLength; i++)
    nLRC += *nData++;
    return (BYTE)(-nLRC);
    } // End: LRC
    CRC Example Code
    This function is an example how to calculate a CRC word using the C language.
    WORD CRC16 (const BYTE *nData, WORD wLength)
    static const WORD wCRCTable[] = {
    0X0000, 0XC0C1, 0XC181, 0X0140, 0XC301, 0X03C0, 0X0280, 0XC241,
    0XC601, 0X06C0, 0X0780, 0XC741, 0X0500, 0XC5C1, 0XC481, 0X0440,
    0XCC01, 0X0CC0, 0X0D80, 0XCD41, 0X0F00, 0XCFC1, 0XCE81, 0X0E40,
    0X0A00, 0XCAC1, 0XCB81, 0X0B40, 0XC901, 0X09C0, 0X0880, 0XC841,
    0XD801, 0X18C0, 0X1980, 0XD941, 0X1B00, 0XDBC1, 0XDA81, 0X1A40,
    0X1E00, 0XDEC1, 0XDF81, 0X1F40, 0XDD01, 0X1DC0, 0X1C80, 0XDC41,
    0X1400, 0XD4C1, 0XD581, 0X1540, 0XD701, 0X17C0, 0X1680, 0XD641,
    0XD201, 0X12C0, 0X1380, 0XD341, 0X1100, 0XD1C1, 0XD081, 0X1040,
    0XF001, 0X30C0, 0X3180, 0XF141, 0X3300, 0XF3C1, 0XF281, 0X3240,
    0X3600, 0XF6C1, 0XF781, 0X3740, 0XF501, 0X35C0, 0X3480, 0XF441,
    0X3C00, 0XFCC1, 0XFD81, 0X3D40, 0XFF01, 0X3FC0, 0X3E80, 0XFE41,
    0XFA01, 0X3AC0, 0X3B80, 0XFB41, 0X3900, 0XF9C1, 0XF881, 0X3840,
    0X2800, 0XE8C1, 0XE981, 0X2940, 0XEB01, 0X2BC0, 0X2A80, 0XEA41,
    0XEE01, 0X2EC0, 0X2F80, 0XEF41, 0X2D00, 0XEDC1, 0XEC81, 0X2C40,
    0XE401, 0X24C0, 0X2580, 0XE541, 0X2700, 0XE7C1, 0XE681, 0X2640,
    0X2200, 0XE2C1, 0XE381, 0X2340, 0XE101, 0X21C0, 0X2080, 0XE041,
    0XA001, 0X60C0, 0X6180, 0XA141, 0X6300, 0XA3C1, 0XA281, 0X6240,
    0X6600, 0XA6C1, 0XA781, 0X6740, 0XA501, 0X65C0, 0X6480, 0XA441,
    0X6C00, 0XACC1, 0XAD81, 0X6D40, 0XAF01, 0X6FC0, 0X6E80, 0XAE41,
    0XAA01, 0X6AC0, 0X6B80, 0XAB41, 0X6900, 0XA9C1, 0XA881, 0X6840,
    0X7800, 0XB8C1, 0XB981, 0X7940, 0XBB01, 0X7BC0, 0X7A80, 0XBA41,
    0XBE01, 0X7EC0, 0X7F80, 0XBF41, 0X7D00, 0XBDC1, 0XBC81, 0X7C40,
    0XB401, 0X74C0, 0X7580, 0XB541, 0X7700, 0XB7C1, 0XB681, 0X7640,
    0X7200, 0XB2C1, 0XB381, 0X7340, 0XB101, 0X71C0, 0X7080, 0XB041,
    0X5000, 0X90C1, 0X9181, 0X5140, 0X9301, 0X53C0, 0X5280, 0X9241,
    0X9601, 0X56C0, 0X5780, 0X9741, 0X5500, 0X95C1, 0X9481, 0X5440,
    0X9C01, 0X5CC0, 0X5D80, 0X9D41, 0X5F00, 0X9FC1, 0X9E81, 0X5E40,
    0X5A00, 0X9AC1, 0X9B81, 0X5B40, 0X9901, 0X59C0, 0X5880, 0X9841,
    0X8801, 0X48C0, 0X4980, 0X8941, 0X4B00, 0X8BC1, 0X8A81, 0X4A40,
    0X4E00, 0X8EC1, 0X8F81, 0X4F40, 0X8D01, 0X4DC0, 0X4C80, 0X8C41,
    0X4400, 0X84C1, 0X8581, 0X4540, 0X8701, 0X47C0, 0X4680, 0X8641,
    0X8201, 0X42C0, 0X4380, 0X8341, 0X4100, 0X81C1, 0X8081, 0X4040 };
    BYTE nTemp;
    WORD wCRCWord = 0xFFFF;
    while (wLength--)
    nTemp = *nData++ ^ wCRCWord;
    wCRCWord >>= 8;
    wCRCWord ^= wCRCTable[nTemp];
    return wCRCWord;
    } // End: CRC16
    Download Source Code C#
    MODBUS® Protocol.rar
      Link không down được bạn à, check lại nhé!thank!
      mail:dqnam952@gmail.com
        MODBUS RTU.exe
          Nguyên văn bởi katllu Xem bài viết
          Cho mình xin cái source code được không bạn, mình đang cần gấp..... Cảm ơn bạn trước nhé
          katllu THIẾT KẾ CÁC PHẦN MỀM ĐO ĐẠC, GIÁM SÁT VÀ ĐIỀU KHIỂN Tìm hiểu thêm về katllu